Postby gekosin » Sun Nov 23, 2014 10:10 pm

Hi all,

I bought an rc -112e temperature controller and am just a bit confused about how to wire it.

I followed the diagram supplied but am not sure what the normal close is for.

Wired it as follows for now but it does not seem to be working
1 + 2 load
3 empty (normal close)
4 + 5 sensor
6 + 7 power

Any advice would be great. Thanks.
Proud Parent Of -

4.0.0 Corn Snake (Ghost Striped, Anery, Amber Stripe Corn)
0.3.0 Corn Snake (Normal, High Bloodred, Motley Gold Dust)
gekosin
SA Reptiles Member
 
Posts: 476
Joined: Tue Apr 10, 2012 3:12 pm
Location: Benoni, JHB

Re: rc-112e

Postby Superciliaris » Mon Nov 24, 2014 8:14 am

Hi

How is it not working , is it lighting up ie is their power to the device ? or is their power but the sensor doesnt work ?
Bear in mind these devices come as 110v or 24DC and various other formats. You need the 220v version , do you have the 220v version ?

Hope this helps
Andrew
Life is the greatest adventure imaginable.
User avatar
Superciliaris
SA Reptiles Member
 
Posts: 215
Joined: Mon Mar 16, 2009 10:59 am
Location: Durban

Re: rc-112e

Postby gekosin » Mon Nov 24, 2014 9:41 am

Hi Andrew,

Apologies for not explaining properly. The device powers on and i am able to "set" the temps but it does not seem to be heating, i do have the 220v variant. The device is currently reading 20 degrees (confirmed with a thermometer),

I set the device as follows
HC - set to H
low temp - 30
high temp - 35
Proud Parent Of -

4.0.0 Corn Snake (Ghost Striped, Anery, Amber Stripe Corn)
0.3.0 Corn Snake (Normal, High Bloodred, Motley Gold Dust)
gekosin
SA Reptiles Member
 
Posts: 476
Joined: Tue Apr 10, 2012 3:12 pm
Location: Benoni, JHB

Re: rc-112e

Postby Primogen » Mon Nov 24, 2014 10:58 am

Change your load to work on 1 and 3 so that the load is normally on(closed circuit) but turns off when relay turns on(reaches temp).
“The animal needing something knows how much it needs, the man does not.” — Democritus
User avatar
Primogen
SA Reptiles Member
 
Posts: 507
Joined: Wed Oct 10, 2012 3:08 pm
Location: Germiston, Dawnview

Re: rc-112e

Postby Primogen » Mon Nov 24, 2014 11:43 am

Before you do what I said on the previous post, On pins 1,2 and 3 do any of them say C, COM or Ground?
“The animal needing something knows how much it needs, the man does not.” — Democritus
User avatar
Primogen
SA Reptiles Member
 
Posts: 507
Joined: Wed Oct 10, 2012 3:08 pm
Location: Germiston, Dawnview

Re: rc-112e

Postby gekosin » Mon Nov 24, 2014 12:44 pm

I will take a closer look at the device but i dont recall seeing anything like that,

this is a link to the diagram they gave me to work off

http://www.sareptiles.co.za/gallery/displayimage-22793.html
Proud Parent Of -

4.0.0 Corn Snake (Ghost Striped, Anery, Amber Stripe Corn)
0.3.0 Corn Snake (Normal, High Bloodred, Motley Gold Dust)
gekosin
SA Reptiles Member
 
Posts: 476
Joined: Tue Apr 10, 2012 3:12 pm
Location: Benoni, JHB

Re: rc-112e

Postby Primogen » Mon Nov 24, 2014 12:57 pm

The diagram shows pin 2 is COM so you must connect you heater to pins 2 and 3.

If you connect pins 1 and 2 that's basically for cooling because your load will only turn on when you hit your set temps.
“The animal needing something knows how much it needs, the man does not.” — Democritus
User avatar
Primogen
SA Reptiles Member
 
Posts: 507
Joined: Wed Oct 10, 2012 3:08 pm
Location: Germiston, Dawnview

Re: rc-112e

Postby gekosin » Mon Nov 24, 2014 1:45 pm

thanks a mill will give it a try tonight when i get home
Proud Parent Of -

4.0.0 Corn Snake (Ghost Striped, Anery, Amber Stripe Corn)
0.3.0 Corn Snake (Normal, High Bloodred, Motley Gold Dust)
gekosin
SA Reptiles Member
 
Posts: 476
Joined: Tue Apr 10, 2012 3:12 pm
Location: Benoni, JHB

Re: rc-112e

Postby gekosin » Mon Nov 24, 2014 6:40 pm

Thanks for the assistance. Still don't seem to be coming right though. I went as far as testing the hearing pad to make sure it works. The thermostat is currently reading 23 but won't go higher...
Proud Parent Of -

4.0.0 Corn Snake (Ghost Striped, Anery, Amber Stripe Corn)
0.3.0 Corn Snake (Normal, High Bloodred, Motley Gold Dust)
gekosin
SA Reptiles Member
 
Posts: 476
Joined: Tue Apr 10, 2012 3:12 pm
Location: Benoni, JHB

Re: rc-112e

Postby Foxticity » Wed Nov 26, 2014 9:51 am

Howsit

I sell the STC 1000 which is very similar but has a cooling function aswell.
I have attached a quick wiring diagram for them that should work on your thermostat aswell
If you still don't come right, add me on whatsapp then ill send you photos of the wiring.

Cheers
Michael
082 401 6667
You do not have the required permissions to view the files attached to this post.
User avatar
Foxticity
SA Reptiles Member
 
Posts: 137
Joined: Thu Jun 16, 2011 10:06 pm
Location: Alberton(jhb)

Re: rc-112e

Postby gekosin » Wed Nov 26, 2014 10:03 am

Thanks a mill Foxticity, I actually got hold of Rolf and he was kind enough to send me a photo of how it is wired, very similar to what you have above :) please to say i did get the unit working last night. I will post the photo Rolf sent me a bit later as im sure it will come in handy to someone in the future.
Proud Parent Of -

4.0.0 Corn Snake (Ghost Striped, Anery, Amber Stripe Corn)
0.3.0 Corn Snake (Normal, High Bloodred, Motley Gold Dust)
gekosin
SA Reptiles Member
 
Posts: 476
Joined: Tue Apr 10, 2012 3:12 pm
Location: Benoni, JHB


Return to Electrical accessories & techniques

Who is online

Users browsing this forum: No registered users and 1 guest

cron